Range hood ductwork through crawl space?

I'm looking at a new house that has what appears to be a pretty nice kitchen, including a nice hood over the rangetop. I open up the cabinet above the hood and see a nice 8" duct, but it takes a 90 degree turn and goes into the wall, and after that, you cannot tell where it goes.


So I talk to the builder. Turns out, it then goes down into the crawl space and terminates to the exterior.


So it goes up, then takes a right angle turn to go horizontal through the wall, and then apparently takes another 90 degree turn to go back down to the crawlspace, and then apparently takes at least one more 90 degree turn to go horizontal again to make it to the outside crawl space wall.


Am I correct that this is a highly disfavored way of running a range hood duct? Seems like having a minimum of three 90 degree turns (including one that is effectively a 180 degree "U" turn) would seriously diminish the effectiveness of the vent?


And, as an aside, this is a brand new building company. The owner has been in the industry for about 20 years but just recently created this company. The choice for how to run the range hood duct work makes me wonder if they made other weird decisions in the construction of the house. Is that a valid concern or am I being too picky?

コメント (18)

  • writersblock (9b/10a)
    6年前
    最終更新:6年前

    I don't know where you are, but in FL "crawlspace" is another word for attic, because that's all they mostly are. Is it possible that's what they mean?

  • PRO
    Anglophilia
    6年前

    That's a new one. I think it would put cooking odors and moisture throughout your entire house. Yes, I'd wonder what other "creative" things they did to this house.

  • Nothing Left to Say
    6年前
    最終更新:6年前

    Everywhere I have lived crawlspace is underneath the house, where you don't have a basement. I've never heard it used to mean attic.

  • writersblock (9b/10a)
    6年前
    最終更新:6年前

    In FL it can mean either one, but since post-WWII houses are usually built on slab here, nowadays the latter meaning is much more common. Under-house crawlspaces existed back when houses had real attics that you walked up stairs to get to and could stand upright when you got there. Those houses were usually on a slightly raised foundation to allow air to circulate beneath and also in case of flooding.

    Anyway, I'd be curious to hear from anon if this is (hopefully) a possibility. Otherwise, I'd have to agree with Anglophilia--time to worry.

  • just_janni
    6年前

    Considering the OP used the word "down" a few times, I am thinking we're talking about the "lower" crawlspace definition.

    And yes - this is downright bizarro. I would anticipate that being 100% ineffective.

  • User
    6年前

    That’s a PASS on that house. If they’d do that, there are likely stupider things that you can’t see.

  • cawaps
    6年前

    I thought that writersblock was suggesting that the OP may have misunderstood what the builder meant when they said crawlspace; that s/he understood the crawlspace under the house when the builder meant attic crawlspace.

    If the duct has 3 90 degree bends and runs an extra 7 feet to get from the hood down to the crawlspace under the house, yes it's a problem. It's bad system design and will adversely affect the performance of the fan. CFM rating is based on a specific static pressure, and the longer your duct and the more bends it has, the worse the performance will be (lower CFM).

    But if there's any chance that there was a miscommunication between you and the builder, I would try to get clarification before I wrote off the house.

  • writersblock (9b/10a)
    6年前

    I thought that writersblock was suggesting that the OP may have misunderstood what the builder meant when they said crawlspace; that s/he understood the crawlspace under the house when the builder meant attic crawlspace.

    Yes, exactly. Thanks, cawaps.

  • palimpsest
    6年前

    When I moved into an upper floor unit in my condo, I became knowledgeable about the ventilation ducts from people's range hoods because I had to move a couple of them and not add to their equivalent length.

    I determined that the duct length from my lower floor unit was 40feet in a purely vertical direction and had three 90 degree elbows for a total of 55 feet equivalence.

    The range hood I had had a 60 foot total allowable length. It was noisy, but it did work because it (barely) met the total overall length requirements.

    I am not recommending maximizing duct length and the number of bends by any means, but I am just pointing out that you can't assume that it won't work just by looks. You have to calculate. And a sealed duct should still carry cooking smells and vapors out and not allow them to "leak" into the house. Anecdotally I think that since grease is heavy there will be some settling of grease on long horizontal runs of ducts internally toward the outlet.


  • Fori
    6年前

    I've seen this in homes that were built with a downdraft and retrofitted with a wall hood. Works okay (not great) but I can't imagine building it that way on purpose!

  • palimpsest
    6年前

    I took out a downdraft duct like this that ran the length of the house and replaced this with an island hood but it took 4 bends to get it the short distance out of the house.

  • Anon Username
    質問の投稿者
    6年前

    OP here. Thanks for the feedback. This is in NC where "crawl space" means the area below the house when it does not have a basement. In NC attics are called attics. Builder definitely says this goes through the crawl space and vents to the outside.


    And this is new construction, so no, it was not a downdraft retrofit.

    Even if they calculated the length of the ductwork correctly to account for all of the 90 degree turns, it still seems like the majority of folks think this is a questionable building/design choice, and I tend to agree.

  • Fori
    6年前

    Test it out. It might be okay.

  • palimpsest
    6年前

    The next question is, where would it have gone otherwise? If the builder ignored several obvious shorter routes for the crawlspace, maybe it is a questionable decision.

    But if it goes through the crawlspace to avoid blasting someone in the face on a deck or patio or to avoid a vaulted ceiling upstairs from the kitchen or some other convoluted path, maybe it is the better of several not great options?

    (My house has corner to corner glass on both front and back elevations on the first floor and a glass wall with exposed sheathing ceiling on the third floor. (And common wall houses on each side). There are very few places to run any ducts.We are fishing a vent duct straight up and through a knee wall that avoids any of the glass walls, but my neighbors have one duct that bumps out in front of one of these windows, and another vent that exits exhaust right next to their front door. Not attractive. We are able to run this duct relatively straight because we are demoing back to the masonry wall between houses.)

  • acspomer
    5年前

    My brother just installed 2 Range Hoods this way going down & out through the crawl space to the outdoors, it is becoming more commonplace to do this, I had never heard of it before & researched it, although I should have known he knew what he was doing, he does a lot of this work & is exceptionally intelligent. I was interested because I want to put in a range hood but don't want to put anan opening in my very expensive metal roof, my crawl space underneath is 5' deep & this is the only way I would consider a range hood that vents outdoors.

  • PRO
    W.K. Shank Design
    4年前
    最終更新:4年前

    We have had to do this up-down-sideways-out scenario in renovations where there just isn't a closet or space upstairs to take a vent though to the roof. As posted above, you just have to calculate how many turns the system and length will allow, and I'd suggest you stay well inside of that limit for good air movement. If I were designing a new house I certainly wouldn't plan it this way, and if the plans called for it I'd wonder more about the designer/architect than about the builder!

  • qofmiwok
    3年前

    Nobody has mentioned the reason this is sometimes a good way to do it. It allows you to use a remote blower which makes your hood much quieter. Yes it could be simpler to go up with it, but not everyone has an attic for the fan, or the ability or desire to put another penetration through their roof.

PR